HOW to speed control of induction mototr using scalar control
Answer Posted / g senthilkumaran
Using scalar control, also called "volts per hertz" control
or v/f control, a drive essentially acts as a power supply
of a selected frequency and proportional voltage. At a
given speed, the motor performs much as it would when
supplied by utility power. For each frequency setting,
motor operation is governed by a torque Vs speed curve that
is similar to the torque Vs speed curve that governs
utility power operation.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
0.5,1,1.5,2.5,4.0.6.0,10,16 square mm electrical wires how much take maximum current in 50htz
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
pls tel me the electric train traction motors name plate details like rpm,torue,voltage,amps,watts..ect..
Where I can get the sample question for post of Junior engineer electrical-II For RRB Bhubaneswar.
How do we calculate over and under frequency tolerance from generator data?
any one please tell taht what type questions will be asked in BHEL interview, i am having interview on 24th Dec, please send this to mail pradeepsistam@yahoo.co.in
TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
What is cut-off rate?
Which type of questions well asked. ?
what is the difference between b c d curves on mcb
Grid fault level [KA]?
What is the function of capacitor in electrical circuits?
how to get electrical supervisour certificate in gujarat
how many current required for hypo test