Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What is difference between earth leakage relay and
restricted earth fault relay ?

Answer Posted / sridhar.u

REF
Windings of many smaller transformers are protected by
restricted earth fault (REF) systems. Even so, I have come
across a lot of installations which would have benefited
from this type of protection, but for whatever reason it has
not bee installed.
The illustration shows the principal of REF protection.
Under normal conditions and by application of Kirchhoff’s
laws the sum of currents in both current transformers (CTs)
equals zero. If there is an earth fault between the CTs
then some current will bypass the CT's and the sum of
currents will not be zero. By measuring this current
imbalance faults between the CTs can be easily identified
and quickly cleared. Fault detection is confined to the
zone between the two CTs hence the name 'Restricted Earth
Fault'.
REF protection is fast and can isolate winding faults
extremely quickly, thereby limiting damage and consequent
repair costs. If CTs are located on the transformer
terminals only the winding is protected. However, quite
often the line CT is placed in the distribution switchboard,
thereby extending the protection zone to include the main cable.

EARTH LEAKAGE RELAY
There is NO particular zone restriction for the normal
Earth
leakage relay which will sense an earth fault or earth
leakage downstream of it.

Is This Answer Correct ?    2 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Do u know any one? how to find out in motor rated amps? formula?

2027


What is different between Circuit breaker and Isolater?

1811


Lt motor sfu flashing reasons?

1783


What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.

2356


what is servo motor & how does it work.

1935


how does the terminal voltage of transmission lines increase when a capacitor is connected???? This happens not only in transmission lines but also in all circuits. How??? When a capacitor is connected in a transmission line, capacitor also takes energy from the same supply. But how is it able to increase the terminal voltage??? Practically What sequence of events happen during increase in voltage???

2176


how to calculate regulation constants for over head lines? and what are the regulation constant for raccoon conductor at different voltage level and different P.F?

1972


i want wipro vlsi placement pattern please send me

1772


What happens if i apply 500V to 440V rotary Switch ?

1831


What are the various types of rotor used in the alternators?

1070


defination of lines

2004


What is the function of NGR for the parallel operation of alternator? whats happen when different rating of alternator are running with parallel?

2980


What is the working mechanism of OLTC in Power Transformers????

4326


dg earth connect only in the amf panel or not why

2087


How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???

2280