Please provide me detail cable voltage drop calculation
Answer Posted / arshadullah
Voltage drop for selected cable
Vd = mV * I * L/N * 1000
Where,
mV : milli Volt
I : CURRENT
L : LENGHT OF CABLE
N : NUMBERS OF RUNS
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
how the inner and outer body is separated in aircrafts?
substation+ plc system
what is the terminal voltage of dc series generator running at rated speed at no load?
if 3400kw slipring motor rotor shorting done and motor started on mv drive ,what will be the rotor shoring current
What are the material used for resistor?
How to set a Zone 1 distance relay for distribution feeder?
my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
How dia computation perfomed in cold rolling mills .
What are the function of different components of servo motor?
What is a parabolic signal?
How many double suspension hardware fittings are required on a double circuit transmission tower?
Explain what is use of lockout relay in ht voltage?
Describe Non I.S. Earth System and why is it used?
how brushed dc motor operating ?