What is mean by vector group? For what purposes we doing
vector group test in transformers?
Answer Posted / muhammad asghar
Vector group contains two things:
1- Scheme of Connection
2- Phase shift between LV and HV windings
For Example, if Vector Group is Dyn11 then
Capital 'D' means HV winding is connected in Delta
Small 'y' means LV winding is connected is star
Small 'n' means LV winding has a neutral also
11 means LV winding is leading HV winding by 30 degree.
| Is This Answer Correct ? | 5 Yes | 1 No |
Post New Answer View All Answers
What do you mean by turns ratio of instrument transformer?
Difference between low impedance and high impedance Restricted Earth Fault
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
in 6.6 kv vaccum circuit breaker vaccum bottole vaccum capacity ????
what is the Pickup/drop off ratio in BCPU relays
How to calculate fault level of 11 KV system
Difference between On Line capacitor and Station Type capacitor.
What is purpose of reactor?.What is different between line and bus reactor?
A 500 V shunt motor runs at its normal speed of 250rpm when the armature current is 200A. The resistance of the armature is 0.12 Ω. Calculate the speed when a resistance is inserted in the field reducing the shunt field to 80% of normal value and the armature current is 100A.
Grid fault level [KA]?
how can we change the polarity of Alternating current rapidly? how frequency of ac can be controlled and changed easily?
how to calculte capacitor range for single phase induction motors??pls tel
What is nyquist contour?
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
What are the main advantages of bode plot?