What is difference between earth leakage relay and
restricted earth fault relay ?
Answer Posted / alialewesy
earth leakage relay can not distinguish the fault location
so that it works for faults inside transformer winding &
outside transformer winding ( drawback)
REF protection has the advantage of distinguishing the
fault location .
it works only for earth faults inside the transformer
winding the transformer will be tripped only for earth
fault insid their winding
th only disadvantage of REF protection is that
it can not cover the whole winding . it protect only 80-85%
of transformer winding
for the reason of CT differences & saturation of CT
so that astand by protection is needed to protect the 15%
of the unprotected winding
| Is This Answer Correct ? | 1 Yes | 3 No |
Post New Answer View All Answers
i applied for the ap transco please forward the freqventley asked QA
how to calculate the earth fault current
why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?
Is there a diode made that works with AC 120 volt 20 amp? If so can it completely stop all current flow in 1 direction at all times?
We have studied about many techniques for finding the stability of system, ROOT LOCUS, ROUTH, BODE PLOT, POLER PLOT etc. In these which is used where. what are the difference among them... PLZ tell me.......
how many safety really of DG sets.
how to electronic energy metter failed in electomagnectic fild passing in the metter and which thing to defect more on metter.
The knee point of a current transformer is normally unique and known.So why in the nameplate of a CT they put the minimum value like this Vk> 400v.
Why 3 phase induction motor getting supply in body if one of it's phase is cut
Why open circuit test of transformers is conducted at rated voltage??Why not any other voltage??
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
why do we carry out winding resistance test?
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
what is the breaking capacity and making capacity of circuit breaker and how
ult of expression 'document.FrmQF.myem