BASICALLY, 1 TON = 12,000 BTU
1 WATT = 3.412 BTU
THEREFORE: 1 TON = 3,516 WATTS = 4.713Hp
CURRENT (Amp) I = Power (Watts) P /Voltage
(volts) V
I = 3,516Watts/240Volts
I = 14.65Amperes
The ans: a)P=3,516Watts
b)I=14.65Amperes
| Is This Answer Correct ? | 77 Yes | 99 No |