how to select the power contactor in Diffrent AC motors.
Answer Posted / sahilsmohan
This is depend of utilization of motor :
A.C motor) A.C 1 to A.C 4 : slightly
inductive,slipring,squirel cage ,starting ,stoping, and
plugging, inching .
DC motor ) DC1 TO DC4 slightly induction, series
/shunt,staring stopping, pluging, inching
| Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
explain why core loss of a transformer is almost constant under different load conditions when connected across a constant voltage and constant frequency.
where is core-type and shell-type construction suitable for transformers ?
What are the three constants associated with a steady state error?
How to calculate the heat load for a electrical room
what is current check gurd relay?
can we synchronize star system generators with delta system generators?
The electromagnetic torque developed is proportional to what in a D.C series motor?
Yazaki india pvt ltd interview questions qurey related
Is it required to lay GI wires along with GI/MS conduits from one point to another point though separate earthing cable is conncted from DB to Socket?
Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station
gas turbine genrator reactances
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
Compare jfet’s and mosfet’s.
how to find the multiplication factor for digital energy meter and analog energy meter