why most of the induction motors are delta connected?
Answer Posted / praveen
I agree with answer 1&2 and second part of 3rd answer.
while designing an ind: motors(IM) starting method has to
be considered and most simple method is star-delta if you
do not have power system capability for DOL(direct on line
starters)starting. for that you have to design it in delta
configuration.
where i work ,most of the IM's are star connected and are
with DOL starters.Wherever delta connected IM is they all
are designed for star-delta starting.
and of course during its normal operation delta has a
marginal(depending on rating)saving in Cu loss and thus
heat load.
| Is This Answer Correct ? | 4 Yes | 2 No |
Post New Answer View All Answers
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
What current flows in the transformer primary when its secondary is open?
State and define norton’s theorem?
Please tell me the earthing procedures adopted for the STAR-STAR 3 Phase transformer in india and give a better sugession for earthing
What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?
why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain
what is difference between earthingpits,earthing grid & earthing mess?
What are the two segments of nyquist contour.
1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?
Does outdoor isolator loose connection cause short circuit current in that circuit? if yes then how ??
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
HOW TO CALCULATE THE REGULATION OF 100 AND 25 KVA TRANSFORMER
what are factors to be consider to design a HT & LT motor?
george phenomenon of synchronous machine
What is the temperature PROFILE OF A FLUID W. R. T. Distance from a sphere to which it is IN CONTACT which is at constant temp.?