Answer Posted / gopal manda
the principle of excitation is that,it is same as low
voltage dc generator,to generate high voltage,we need very
strength static magnetic field,which we creat by external
dc voltage, produce by ac or dc generator.so we excite the
fieldwinding of alternator.
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
diff.between servo motor and ac motor
how can i use REF and diffrencial relay both in 1 CT core for transformer protection?
What are the advantages of nichols chart?
What should be the protection scheme for a 15kw, 3-phase motor working in a lathe machine.
What is the maximum number of swithes that can be connected in series up to down stream point in an LV Distribution system?
specific difference of ICT&Auto Transformer
I WANT TO INSTALL LIGHTING ARRESTOR ABOVE 20 FEET HEIGHT INDUSTRIAL BUILDING. NOW IT WAS 15 FEET HEIGHT HOW MUCH DISTANCE IT WILL COVER & HOW TO CALCULAT THE DISTANCE COVER BY THE ARRESTOR
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
How can we find out LT UG cable fault (size,from-4*25mm sqr to 4*300mm sqr)? How mani types UG cable faults?
List the power rating of any 5 important electrical appliances used in houses.
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?
If oil and air can withstand a high MeV when used as an insulator in a transformer, what are the values of how high for each material?
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .