How can we check ELCB trip current sensitivity
How can we check earth resistance value
Answer Posted / william lobo
Elcb is earth leakage circuit breaker. There are many
sensitivities in India. popular are 30ma, 100ma, 300ma,
500ma. For getting the correct corelation as to which
sensitivity is to be used for what application, it is
necessary to understand the effect of electric current on
the human being. I have the chart which shows the effect of
different ma current flowing through ones body and the
result. Usually below 30ma current is safe and gives only
tingling sensation to the person. But above 300ma can prove
dangerous and heart will stop.
For the second part you can use an earth megger and
connections are provided on any website or send me a mail
williamloboatrediffmaildotcom.
| Is This Answer Correct ? | 20 Yes | 2 No |
Post New Answer View All Answers
how to select the isolation tranformer for siemens 802dsl cnotroller
What are the three constants associated with a steady state error?
what is interfacing in computer studies?
what is is the potential diffrence between two phase ?
What is the difference between electrical earthing and electrical grounding?
how load of a turbo generator can be increased
On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?
internally connection of photvoltic module
what is the best transformer oil breakdown voltage?
What is the effect on 3phase induction motor if current setting knob of DOL kept at minimum current?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice
How work of capacitor in dc supply...???
how to find three phase complex power in per unit and MVA?
CPC cable .PVC \1C....I want to get sure that type is flexible indoor or to be install on trench. please advice .thanx :)
help me with the question that might be ask on the interview for technical position