What is the function of automatic Transfer Switch(ATS) in
details

Answer Posted / gopal varsani

ATS is the Automatic Transfer Switch, The function of this
switch is that if the utility supply goes then the
connected equipment would be transfer automatic on
emergency source from utility source through this switch.

But it is programed few second delay asper sefty rules becose
when incoming flickering or sparking that time it should not go on where incoming sores are connect healthy that switch may go on

Is This Answer Correct ?    18 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

The power factor of the fixed load is 0.8, now the p.f is varying from 0.8 to 0.5.

1572


How to calculate cable rating for 3 phase supply?

1713


What are linear and non-linear systems?

644


can we use NPT glands in LT panel

1320


As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?

1396






What is “pu” in electrical engineering?

675


what is per unit calculation?looking for simple and strong explanation thk u

2074


How to check the thermocouple is correctly connected to cable for K type? (i,e positive pole is connected to non magnetic conductor and negative pole is connected to magnetic conductor)

1252


How to test lightning Arrester?

398


why we change the direction of winding in rotor ?how we make the north and south pole?

1578


What are the significant parts of dc generator?

629


i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.

1571


How generating electric power export to grid from the generating station ?

1405


can mini-curcuit supply MIL-tested transformer !

1617


how harmonics generated in induction furnance? how minimise it?

1528