what is the radio of kva & kvar or why calculated kva & kvar
Answer Posted / ayan
I guess its a typo..and instead of radio it should be ratio.
The ratio of the Kva & Kvar is the sine of angle Φ ,
considering in the power triangle the base/adjacent is "KW",
the opposite is Kvar and the hypotenuse is the representing
KVA and Cos Φ is power factor.
Power is represented in KVA and KVAR because of presence of
Power factor and Reactive power.
| Is This Answer Correct ? | 6 Yes | 0 No |