What sort of protection scheme do you suggest for the
protection of a 10 HP motor?
Answer Posted / raghavendran.r
1)Instantaneous overcurrent protection.
2.Ground fault protection.
3.Thermal overload protection.
4.Stalling Protection.
5.Phase unbalance protection.
| Is This Answer Correct ? | 14 Yes | 0 No |
Post New Answer View All Answers
what is through fault?
what curve and rateing would you use for a three phase 0.75kw motor?
what's the difference between 'shaft power demand' and 'BHP' , when we consider electrical load list.
Difference between ac parallel circuit and ac series circuit?
How we select the vector group of 3phase power transformer?
is it possible to test of bus bar in high rise building without completed full floor ?
What is dynamo?How it works and what is the function of dynamo in a DG.
in indoor type circuit breakers why only the corner breaker trips specially during cold season. What is the reason.
which connection is safer series or parallel?usually which connection we prefer at home?
What is DC series motor?
what is effect of leading power facter on the system and billing
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
percetans
I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.
How can we increase fuel-power ratio of any DG set?