A resistance, inductance & capacitance are connected in
series between points A & B.The voltage drops across the
resistance,inductance&capacitance are found to be
40V,70V&100V respectively. What is the total voltage between
between points A&B (Vab)?
a)210V b)70V c)50V d)230V
Answer Posted / n.k.singh
50 Volts
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
What is fault clearing time for Current Limiting Moulded Case Circuit Breaker?.
How relay coordination has to be done? what are the inputs are required for this? Please explain this with calculation method?
Explain the working of any one cutting machine
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
BRIEFLY EXPLAIN THE STORAGE CLASSES AND THEIR TYPES IN C
What are the types of transformers according to the arrangement of iron cores?
how many joint can done in HT line and what is life of the joint
Explain how you decide what size of electrical wire do you need?
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
how we test a 3 phase motor on single phase supply....? HOW WE RUN A 3 PHASE MOTOR ON SNIGLE PHASE. supply for testing..? how we verify of a 3 phase motors 6 wire & name thame a1/a2/a3..b1/b2/b3 and c1/c2/c3 for connecting star delta starter ........i have only 1 phase supply ? help forum..........
I had applied for JE in PSEB, Can you pls send me the Question bank for related to my field
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
can u give me a brief idea about power line carrier communication ??
What is the difference between Droop vs Isoch Control?