Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

if AVR fails in D.G set, what will be the effect?

Answer Posted / abdul ghani fatima fertilizer

Dear Friends.
If Generator is running in Island mode then it will be
tripped due to excitation failure so all the load will be
cut off, and if the Generator is running in Parallel even
then it will be tripped on under excitation.

But if the excitation protection fails then it will be
tripped on reverse power.

And if there is no any protection then during parrallel
running the faulty generator shall act as motor, and if
Generator running in Island mode it will be continuous run
without output rated voltage so loads shall not be
continued.

Is This Answer Correct ?    6 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the advantages og idmt relay over magnetic relay??

4253


What is the distance between each insulator in 33kv transformer and how can it calculate

2200


how to conduct dc resistance test for rotor of an alternator and how to measure the rotor dc resistance value theoritically?

3304


I am shobana from Chennai. I am having my personal interview on 19th Dec at Chennai.kindly mail me the questions to mail id shobana.shanthi@gmail.com

2381


Please explain me about Relay curves and their sources to read ?

1821


what is the difference between linear choke and suction choke?

2751


Is vtg is controlled by the resistor? if else how much?

2100


When semiconductor fuse does save thyristor in each cycle of conduction? Why under voltage setting keep less in SPRS and more in DC drive?

2102


is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.

1718


how can we find thae value of capacitor for single phase motor. what is difference between starting capacitor and running capacitor.

2386


What are the advantages & disadvantages of a group electrive drive?

2159


do we use neutral grounding for resistive balanced load? if we use what happen?

1803


What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?

2260


According to conduit size which size wiring & how many wires can we provide wires in conduit & how can we select conduit size accordingly?

1909


What is gross error?

1152