if we convert kva into Ampers,which one formula use by
us,pls tell me?

Answer Posted / virendra joshi

KW = KVA*Pf

W = KW / 1000

W = 1.73 x VL x IL x PF

I = w / 1.73 x VL x PF

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.

1462


May I know how much values to be set for earth fault, over current and short circuit values at 11kv side? I have 11kv van 1250amps rating. Present it's taking load 80amps?

1020


Define transfer function?

741


Explain Circuit Breaker Trip Characteristics in detail.

1669


what is meaning of 230volts ac 50hzs ac supply is it rms or maximum to getting ac 230v what amount of max voltage they will send

1540






for what voltage will reactive power be largest in 380 kv line : a) 375kv b)380kv c)385kv

988


what will be the effect if you were using different brands of outlets?

1466


if we have 320KVA Genset kindly advice how much load we can put it.

1010


what are the values of VRY,VYB,VBR,Vry,Vyb,Vbr,Vrn,Vyn,Vbn for Magenetic balance test of 100 KVA and 63 KVA Distribution transformer

2423


what is saturation kit?which use above 15 kw motors panel side.

3568


what are the accessories need to be added while doing estimation for the following: 1.MCCB 2.MCB 3.ACB

1573


how to select automotive wire by mathematical equation with given current, vlotage and resistance

1898


hi frnds what is meant by harmonics & what is meant by third hormonics,where its will occur ?thank u

1517


explain the Trip supervision circuit

1654


If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.

1487