1. what is difference between VCB and ACB.how its works
please explian.
Answer Posted / n. gopala krishna
difference between vcb and acb. vcb is vacume circuit
breaker acb is air circuit breaker . in vcb switching
contacts fixed in vacume cylender. in acb switching
contacts arranging in openly in airbut other all mechanisim
is same both breakers having closing coil and tripping coil
and spring charge motor all are having but vcb breakers
using in high voltage side to reduse the arc at on off
time. but acb can use in low voltage side only
| Is This Answer Correct ? | 85 Yes | 21 No |
Post New Answer View All Answers
What is the type of feedback used in an op- amp schmitt trigger?
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
why are u join ntpc
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
Which motor is 3.3 or 11kV more reliable, in terms of efficeancy,maintenance, reliability.
How to calculate ant test the burden of Current transformer
Define end float in a motor?
what is harmonics? what are the factors it will depend upon
Mention how NPN and PNP transistor works?
What is a signal flow graph?
1) Explain why we don't link the two earthing system ht and mv on a pole mounted transformer sub-station.
Star Delta Diagram with full description
Can anybody post questions asked in Engineers India Limited Interview? Thanks in advance.
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system