Answer Posted / farhan hashmat
ELCB mean earth leakage circuit breaker,and it is the old
name of RCCB(Residual current circuit breaker, further ELCB
is voltage depended operation and RCCB is current depended
phenomena.and MCB is miniature circuit breaker which is
operated on thermal or magmatic effect of current.
| Is This Answer Correct ? | 40 Yes | 7 No |
Post New Answer View All Answers
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
What is the difference between voltages or potential difference? And what are they?
internally connection of photvoltic module
what is the difference between directional & non directional earth fault with example please explain.
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
model question paper for supervisor trainee
How can we calculate the transformer rating if the load calculated is 1000KW (11Kv Supply)?
how does a liquid starter reduce the starting currents?
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
what is the difference between active power and reactive power and apparant power in practical as well as theoritical
how to produsing geretor power
What is servo motor? what is its purpose?
sometime battery charged and then automatically charged when rectifier ON conition, is there any chances please clarify the same.
describe the Operation of induction generators from bus bars
DRAW ACIRCUIT DIAGRAM OF 100 KVA 415V/55-0-55V DELTA TO STAR TRANSFORMER