In one village i have seen Earthing transformer's earthing
line was also connected to the Transformer body to ground
the transformer,can it be possible to maintain 0Volt
reutral line this way?
Answer Posted / ansarelectrapower
distribution transformers are mainly used
delta/star .HTside is delta
LTside is star because star point is earthed.mainly two
conductors are connected through the transformer
neutral .that is body earth and one conductor coming
directly from earth pit.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what is lumped and distributed elements?
Draw the single line diagram of the power station?
Stator of 3-phase IM has 3 slots per pole per phase. If supply frequency is 50 Hz, calculate the speed of rotating stator flux A 1000 rpm B 500 rpm C 1500 rpm D 1440 rpm
Draw the vector diagramme for Asynchronous Induction Generator at noload,half load and fullload.
What is the two pole structure?
what is the difference between droop mode and ischnorous mode in thermal powerplant?
what is earth-fault?when it occurs? to check where it occurs what type of test should we do?
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
Should power factor be low or high?
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
hi can any body send me syllabus of rrb electrical section engg... and past pepar also of any board...
why do we use spark detector inside the slip ring brush compartment 0ona slip ring induction motor?
Why is a plain induction motor unsuitable for wide speed control?
What is the function of retrip in busbar?