How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answer Posted / uday
1500kVA X 0.8 PF = 1200Kw = 1200000W
P=RT3 V I COS fi
SO, P
I = -----------
RT3 x V x COSfi
1200000
I = -----------------
1.732x1100x0.8
= 79 A
Now take cable table and select the suitable xlpe cable.
Uday
| Is This Answer Correct ? | 46 Yes | 51 No |
Post New Answer View All Answers
What is the difference between isolators and electrical circuit breakers?
What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.
What is the practical way to calculate the cable size for known ampere load?
how to calculate the tarriff for an industry whose kva demand is 10 mva
How to calculate the multiplying factor for energy meter with ct ratio given
What is the function of Governor in Hydro Power Station? What is the Function of Lightning Arrestor Voltage Transformer (LAVT)?
what is the difference between electrical choke and electronic choke?
What is speed mode?
operation of protection relay watchdog contact?
What are the different losses In a de mac1une'! t.xplam
Define open loop control system.
compare between starting charactristics of synchronous motor with those of 3Q Squirrel cage induction motor
how do you test tachos and servos
What are root loci?
why the frequency and voltage in india is 230v and 50HZ. when compared to USA say 110v and 60 HZ.