Answer Posted / haribalakrishnan
For Example if we take 110v Battery bank...Normally in
commissioning time we will put in Boost charge mode in
charger to charge the battery bank, that means we have
charge the battery upto the specified limit given by the
manufacturer,for 30hrs duration.The voltage is around
154v...after that it will come to float mode it maintain
the constant voltage 115V..Normally batteries are in
floating mode only..Only at the time of Initial charging
and if suppose batteries are drained then only we put it in
Boost charge mode....
| Is This Answer Correct ? | 26 Yes | 5 No |
Post New Answer View All Answers
why on delay timer used for fully automatic star delta starter?
hi can any body send me syllabus of rrb electrical section engg... and past pepar also of any board...
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
What is the difference between a fuse and a breaker?
What are the temperature elements?
IN 1000kva transformer where the oil and winding temperature sensors is connected
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
what is the standard values(Megger test) of resistances between L&N,L&E and N&E for a system on IEE regulations?
How to select HT/MV cable size ?
HOW TO CALCULATE HV CABLE SIZING?
Wt is the function of reactive power? How it generates & consume though resultant is zero?
What is the minimum distance to be maintained in between HT panel and LT panel and Instrument panel as per IEC and NEC standards?
State angle criterion.
how does grading rings & spacers in transmission line works? Working Principle?
why current is constant on d.c?