How many types of Control Modes in process control, plz
tell me all.....?

Answer Posted / sam

There is only two modes of control if you really think about it.
On/Off Control and PID Control.

Where some confusion can come in, is when you look at he
various CONTROLLER modes available on a DCS.
PID controllers are also sometimes linked together like in
cascade or feed forward control configuration, but the
control modes is still PID control.

Look at On/Off control:
You can have a open/close control valve in the field that is
controlled by the ESD or DCS system that will either open or
close this valve.
The ESD system do not do any control but it can open or
close a valve during a emergency as a step in it's blow down
or shut down sequence. This is in general not consider as
control just a action.
You can also have another open/close control valve in the
field that is controlling the level in a tank. In this case
it is connected to a Decap controller in the DCS. a Dcap
controller have a set-point that can be set to control the
level of the tank, but if a on/off valve is used as is, this
valve will open and close all the time to try and keep the
level on the set-point. So to prevent this the controller
have a small dead band around the set-point that can be
adjusted. This will then prevent the valve from opening and
closing until it reaches the dead-band threshold position.
Normally about 5% over and under the set-point. It is still
on/off control.

Looking at PID control:
Any mode in conjunction with proportional control is
possible on a PID controller it just depends on the
application. For example PID, PI, PD, P.
You can see them each as individual control modes if you
want, but I prefer to just stick to PID or on/off control
modes since there is a definite and distinct control mode
difference between the two. I see Dcap, PI, PD and P modes
as sub divisions on the two main control modes.
P = Proportional
I = Integral
D = Derivative
Good Luck

Is This Answer Correct ?    5 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How is automatic reference junction compensation carried out in temperature recorders?

635


Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?

10394


How many are the types of instrument cables in terms of No. of pair.

1699


Difference between 2-Valve Manifolds, 3-Valve Manifolds and 5-Valve Manifolds 3 with diagram

2680


key phaser where is use and work

1453






why we are not using the turbine flow meter in the steam service?

1703


why we are using drum level control valve air to close?

1596


How u measure the massflow in orifice flow measurement techniques

981


Give an example where you had aproblem on the job, and tell me how you solved the problem. and the finalvoutcome.

1802


Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer

4164


What is the constant voltage unit?

633


if my flow is 20000 m3/h than which range of DPT i have to use????

1286


what are the diff. in servo and regulatory control?

3464


Why we are using DPT(Differential Pressure Transmitter) in separator instead of level trasmitter?

1764


sir,would you please send me the Hindustan petroleum corporation limited papers(HPCL).my e-mail ID is ujjwal_sharma1983@yahoo.com

1812