How many types of Control Modes in process control, plz
tell me all.....?
Answer Posted / sam
There is only two modes of control if you really think about it.
On/Off Control and PID Control.
Where some confusion can come in, is when you look at he
various CONTROLLER modes available on a DCS.
PID controllers are also sometimes linked together like in
cascade or feed forward control configuration, but the
control modes is still PID control.
Look at On/Off control:
You can have a open/close control valve in the field that is
controlled by the ESD or DCS system that will either open or
close this valve.
The ESD system do not do any control but it can open or
close a valve during a emergency as a step in it's blow down
or shut down sequence. This is in general not consider as
control just a action.
You can also have another open/close control valve in the
field that is controlling the level in a tank. In this case
it is connected to a Decap controller in the DCS. a Dcap
controller have a set-point that can be set to control the
level of the tank, but if a on/off valve is used as is, this
valve will open and close all the time to try and keep the
level on the set-point. So to prevent this the controller
have a small dead band around the set-point that can be
adjusted. This will then prevent the valve from opening and
closing until it reaches the dead-band threshold position.
Normally about 5% over and under the set-point. It is still
on/off control.
Looking at PID control:
Any mode in conjunction with proportional control is
possible on a PID controller it just depends on the
application. For example PID, PI, PD, P.
You can see them each as individual control modes if you
want, but I prefer to just stick to PID or on/off control
modes since there is a definite and distinct control mode
difference between the two. I see Dcap, PI, PD and P modes
as sub divisions on the two main control modes.
P = Proportional
I = Integral
D = Derivative
Good Luck
Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
How is automatic reference junction compensation carried out in temperature recorders?
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
How many are the types of instrument cables in terms of No. of pair.
Difference between 2-Valve Manifolds, 3-Valve Manifolds and 5-Valve Manifolds 3 with diagram
key phaser where is use and work
why we are not using the turbine flow meter in the steam service?
why we are using drum level control valve air to close?
How u measure the massflow in orifice flow measurement techniques
Give an example where you had aproblem on the job, and tell me how you solved the problem. and the finalvoutcome.
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
What is the constant voltage unit?
if my flow is 20000 m3/h than which range of DPT i have to use????
what are the diff. in servo and regulatory control?
Why we are using DPT(Differential Pressure Transmitter) in separator instead of level trasmitter?
sir,would you please send me the Hindustan petroleum corporation limited papers(HPCL).my e-mail ID is ujjwal_sharma1983@yahoo.com