What is diference between ELCB & ELMCB?Also how its
application for use in design area?
Answer Posted / biju9cr
ELMCB is ELCB+MCB also known as RCBO
ELCB provides protection against earth leakage
MCB provides protection against over current and short
circuit current
| Is This Answer Correct ? | 13 Yes | 1 No |