How many types of relay are present in a VCB and ACB, what
are the tests we can conduct on both breakers and how to
set the relays values
Answer Posted / vijaykumar
Protection of the feeders depends upon the load but not on
the type of breaker used.
VCB-measure the Contact resistance and breaking
resistance,tripping time other mechanical interlockings for
the breaker Mechanisms.
ACB-Check the contact reisitance and the contact tips which
are visible to naked eyes,arching chutes,since air is the
quenching media.
| Is This Answer Correct ? | 12 Yes | 5 No |
Post New Answer View All Answers
ACB & VCB how do work and saftes and how can maintenance in this and parts name show with picture
why co incidence factor considered in transformer sizing?
What are hrc fuses and where it is used?
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
What is meant by celling voltage & current in excitor ?
PLZ EXPLAIN THE INTERLOCKING AND CONTROLLING OF CONTACTORS????HOW CAN I DO THAT?
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
why starting current is high and resistance is almost 0 during the starting of motor dc motor...?
why we use Test Terminal Block in 11 KV and 33 KV electrical panels.
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
I am having dual speed motor of cromton greaves make of 3.7 KW -1400 rpm and 5 KW - 900 rpm. Please let me know groups and winding connction for rewinding purpose.
Disadventage of cable-gland earthing if any ?
how electrical earthing maintenance done in industry?
what r the checklist while installing a 380 kva DG set
What is the most important precaution in any experiment with d.c. Shunt motor?