The speed of electrons as they travel down a copper wire is
measured in millimeters/sec. This speed changes as the
voltage, amperage, wire material, and wire size change. This
is called the "drift velocity".

However, a signal will travel down a wire at slightly less
than the speed of light: ~2/3 light speed in a coaxial
cable. This is the propagation speed. The exact propagation
speed is different for different wire materials. Shielding
of the wire also changes propagation speed. The speed
further changes depending on heat & pressure, though in
general, we don't experience enough difference to notice.

Think of it as the difference between wind and sound. The
movement of the electrons is analogous to wind, which rarely
goes faster than 40 mph, and depends on pressure differences
(applied voltage). Where as the speed of the signal is
analogous to the speed of sound, which is ~700 mph,
depending on heat and pressure (state of the material).

Is This Answer Correct ?    4 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is charger supervision and control supervision?

1515


Hi Everyone ! My Name is Hakim ullah khan please i need formula of Cable Rating because i want to calculate by self without check any Table Chart... Thank you.....

1244


In constant power region of 3-phase IM torque-speed characteristics, if frequency increases flux A does not alter B decreases C increases D none of above

1744


can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?

1760


What is minimum phase system?

659






what should be correct gas pressures to be a 1.5 ac unite

1071


What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer

1332


what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.

1563


What are hrc fuses and where it is used?

723


Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com

1427


Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?

952


will 1050kva DG set withstand for back charge of 16MVA transformer

1457


Differentiate between Zero and Negative sequence current

1441


what irequirment need to be followed when working on live equipment

1305


What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side

967