What is the purpose of lighting Transformer used in
Industries for Lighting illumination? Its necessary or not?

Answer Posted / nishad

Lighting Transformers are used to limit the Fault level in
the Bus of main LT panel by varying the impedance of the
Transformer. If any major fault is occurs, its effect is
affecting only up to the lighting Transformer’s breaker and
it trip itself and prevent the main panel from tripping.
As well as big industries, single phase is not using for
MCC & other equipments. So Neutral is absent in main LT
panel. For lighting purpose we need neutral. So we are
using isolation Transformer for lighting in big industries.

Is This Answer Correct ?    52 Yes 10 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Explain the fundamental difference between emf (electro motive force) and pd (potential difference) ?

635


If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?

1535


how to test power transformer.YNd11

1093


at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?

1377


iam using DM 3251 voltmeter(1 percent accuracy)for 11KV system PT ratio is 11KV/110V.can anybody explain what is the max and min voltage deviation.

1743






Which of the following alternatives will be cheaper (1) A 100 h.p AC, 3-phase motor (2) Four motors of 25 h.p each (3) Five motors of 20 h.p each (4) 10 motors of 10 h.p each explain

2513


5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch

3357


how maney type tempereture measurement ?

1822


Classify drilling machines.

680


PLZ SEND ME SOME UNIQUE PROJECT OF ELECTRICAL ENG (B.TECH)

1514


An impedance of 100 ohms resistance and an unknown inductance is connected across the capacitor. The resulting impedance is a pure resistance of 500 ohms ifω = 10^5 rad/sec. calculate the values of inductor and capacitor.

714


explain Density

640


We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?

1090


State nyquist stability criterion.

635


write down the formula of cable size in RM if current is 50Amp.

916