What is the basic difference among Circuit
breaker,Contractor and Isolator?
Are they different names of same device/equipment?
Answer Posted / iamdon
circuit breaker can make,break and carry current under
normal,short circuit and overloaded condition..It operates
automatically.
contactor can make,break and carry current under normal and
overloded conditions only but not in short circuit
condition.It can operates more no of times without
maintenance.
Isolator can break currnt only through that part of circuit
which is bot carrying any current.It is manually operated..
| Is This Answer Correct ? | 6 Yes | 4 No |
Post New Answer View All Answers
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
what are the steps involved in generator load test?
why the India electrical supply transmission loss is high when compare to us
What is critical disruptive voltage?
What are the advantages and disadvantages of closed-loop control system?
what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
where the lexical paramater will use in fron end?
how to calculate the battery AH
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
how can we calculate the ampacity of the electrical wire/cable. and what are the factors must be considered. pls. elaborate.
What is the actual meaning of thermal power efficiency ?
What is the main purpose of c.f.b.c.boiler
how to calculate compresor capacity?
What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?