what is pressure relief valve in D.G ?state its function?
Answer Posted / mrudang
in DG
i am answering about transfdormer
PRD (pressure relief device) using also in transformer
the function remain same
when the fault occcures in transformer , the oil pressure ,
tank mechanichal preessure affect the transformer ,
when fault occurs the oil temperature is high , and ur oil
expands and pressure will be increase
so u use the PRD for relese the pressure of transformer
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
Why r u using pf panel. what the uses
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
what is the best method of grounding in 30 MW generator?
Where burned of electricity,when,who, & why.
What is CVT and what is relation with wave trap?
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
What is the minimum underground tank size capacity considered for firefighting purpose?
In an ACB shunt trip coil and undervoltage coil operated normally( breaker open and charged). But closing coil not operating untill manually discharge and recharging. Any help.
What is electrical diversity factor in electrical installations?
what is level 2 automation?
write circuit diagram for a motor rotate in forward direction once it started and when pressed the same button it should rotate in anticlockwise.
model question paper for supervisor trainee
WHAT ARE THE DATAS REQUIRED FOR PROTECTION AND METERING AND CONTROL AND LOGIC PREPARATION,HOW TO STUDY THE PROTECTION AND METERING?
If I have Energy Meter Ratio as 100:5 & Also I have CT Ratio as 50:5 then what will be my multiplying Factor(M.F.)