Answer Posted / jaldeep
For signal transmission we are using 4 to 20 mA, because of
following reasons.
1. If you are using 0 to 10 for long distance then
signal will be dropped due to cable resistance you will not
get correct feedback
2. 4 to 20 mA will give correct feedback even for
long distance. It will not drop according to cable
resistance. Only you have to keep loop impedance as per
your field instrument.
3. Open loop, you can easily detect in 4 to 20 mA.
You can program if mA is less than 4 then you can define it
as open loop.
4. For 0 to 10 v input if cable is open then it will
be difficult to identify that cable is open or input is 0
volt.
| Is This Answer Correct ? | 17 Yes | 0 No |
Post New Answer View All Answers
How will you calibrate PID controller? explain with example.
Please can anybody help for control valve sizing step by step procedure?
What is zero elevation and zero suppression?
What is standard procedure of manual mapping in Radar type level transmitter?
whats the abbreviation of IOP? is it instrument of power or input open problem?
i want to find out iffco get test paper
What is the difference between working pressure and calibration pressure of a control valve
what is difference between fork type and capacitance type level switch. where it is using
How to find out the current of two motors having same power consumption but different RPM?
Explain the difference between plc and cnc?
Why grounding is necessary? Give example with diagram.
How to work temperature gauge?
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
How works weighfeeders in cement industry? what is the working principle?