how we can calculate the transformer size.
Answer Posted / tarun
Check the following
1.) Max connected load
2.) Type of load
3.) impedence drop as per IS
4.) Drop for cable used
5.) Load factor
6.) transformer efficency
7.) % loading
8.) provision for future expansion
| Is This Answer Correct ? | 6 Yes | 4 No |
Post New Answer View All Answers
what is RNG in the DG synchronizing by PLC?
WHY THE DIMENSION OF TWO SAME RATED MACHINE IS DIFFERENT ?
is there any phase difference occurs while primary and secondary side mutual induction occurs?
Explain the iniluencc of short circuit ratio on the pert'orniancc of synchronous machine.
why the value of k is more in shell typr transformers?
What is the comparison of PILC and XLPE cable
How To increase Knowledge Of boliler regarding To Only Electrical Field..
If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
how to test the turn ratio of 3 phase transformer using volt meter shoe the curcit diagram.
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
what is the calculation method to design core and winding of a 200kva 3phase distribution transformer?
What is milivolt dop test in Busducts? What is its significance & procedure to do the test?
CBCT selection
what is stper motor