Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is the formular for the calculation of CT'S when
installed as part of a electrical installation so the
correct meter is used

Answer Posted / denzel101

Calculate the maximum current you want to measure from your
system. for example calculate the full load current of a
supply transformer. if the full load current is 200 Amps
and your meters have 1amp rating, choose the ratio of 200:1
CT.

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence

3033


what is maxemo work permit procedure

2252


what exactly commisioning work does in electrical site work... LT side?..

1989


if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .

2116


sir i have cleared the apti test of EIL held on 15th march and my interview will be in new delhi on 2nd june.i will be very much helpful if u help me regarding the type of interview questions comes at EIL.(URGENT.........PLZZZZZZZZZZ...............)

2103


If I want to buy a new Xformer for my plant what are the main parameter will I need to check?

1940


Why induction motor is widely used in industry

2814


What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.

2053


Why transformer used in UPS??

1659


hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.

2781


what types of cable used in underground coal mining?

1527


A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.

1368


When and where resistance earthing is used ? How to calculate the time constant for earth fault

1874


How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?

1995


Power Factor Correction Panel (Manual & Automatic)

2286