How many types of relay are present in a VCB and ACB, what
are the tests we can conduct on both breakers and how to
set the relays values
Answer Posted / s naidu
in a vcb this are main relay
1-phase unbalance relay -2nos
2-earth leakege trip relay
3-TR common fault relay
in acb this are main relay
1-load balancing relay
2-u/o voltage relay
3-earth fault relay
4-master trip realy
this tests are carried out generally on both CB
i-cb in open & close position test
2-continuity of contacts
3-manual closing,electrical closing, remote closing
4-remote tripping though protection relays
5-check spring charging motors are in working
relays calibrated operating characteristics to electrical
circuits.
| Is This Answer Correct ? | 54 Yes | 7 No |
Post New Answer View All Answers
in ring main system we use the isolater b/w transfer bus and main bus if we r not use isolatar than wat will be the effect in our sys.
What is depreciation factor?
what is the formula for computing cable tray size & capacity
what is efficient motors and how it is different from normal induction motors
Show Details FROM:Muhammed Ikram TO:qa@allinterview.com Message flagged Saturday, June 4, 2011 10:07 PMMessage bodyHello all, i want to ask a question to all of you that what is VMM (voltage monitoring module )? how it work,s? i heard somewhere that it compare 1 phase voltage to other phase voltage. but there is also some setting on it. how to set it,s setting. please tell me briefly. Thank,s and Regard,s. Muhammed Ikram.
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
how to extend relay operating timing in 24V dc relay card (without using Timer )
operation of protection relay watchdog contact?
why voltage form factor of PT are increase , when it is ecpected heigher spikes in system. how it is calculated.
number of I/O devices in siemense plc
What are the types of excitation system?
Iwould like to know barc interview questions
How much minimum insulation required between 11kv/3.3kv transformer windings?
what is basic difference betmeen normal & flame proof motor??
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?