How many types of relay are present in a VCB and ACB, what
are the tests we can conduct on both breakers and how to
set the relays values
Answer Posted / s naidu
in a vcb this are main relay
1-phase unbalance relay -2nos
2-earth leakege trip relay
3-TR common fault relay
in acb this are main relay
1-load balancing relay
2-u/o voltage relay
3-earth fault relay
4-master trip realy
this tests are carried out generally on both CB
i-cb in open & close position test
2-continuity of contacts
3-manual closing,electrical closing, remote closing
4-remote tripping though protection relays
5-check spring charging motors are in working
relays calibrated operating characteristics to electrical
circuits.
| Is This Answer Correct ? | 54 Yes | 7 No |
Post New Answer View All Answers
what is the difference between unarmoured & Flexible cable? How to identified?
3phase motor can be used as a Prime mover for alternator.
mccb service sittings be done?
On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?
What is the relation between frequency and motor rpm?
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?
How to test REF relay testing for LV panel as per Kahramaa standard?
why does rotor rotets?
Why transformer used in UPS??
What is the restart inhabit setting in ABB spam150c relay (Motor protection relay)
how can we change the phase angle b/w two phase?
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
how to calculate the change over time for star delta starter for different KW motor?
why lightning arrestor are made in two stack of insulator but why not cvt
how to work droop ct in generating station