what is the working difference b/w softstarter and
Variable frequency drive ?
Answer Posted / satyanarayana gupta
the main function of variable frequency drive is to
control speed of the motor according to the load it just
works as control system with feedback according to that
feed back it will change its speed
where as soft starter it will
just monitor the speed at starting time only
by using vfd's most of power consumtion is reduced
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
cc of scorpio?
why do we not use equivalent voltage source in negative sequence equivalent ckt.
what is meant by loss of field in a DC motor? how a universal motor works?
How the over load setting for HT Motors calculated-provided in Numerical Relay
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
how balanced in star delta connection ?
hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.
what is the working process of over & under voltage relay.
why the name trunking bus PT
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
how works inductive &capacitive sensors?
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
What are the different sign conventions used in electric circuits?
If any cable burnt how can we identify it burnt by high current of high voltage?
All the socket in a room become very hot, the Wall was also became very hot and the earth conductor also became live, what in your view might be the possible causes?