how would you come to know if a transformer is double wound
or auto? note that there is no tag. you are given only a
multimeter.
Answer Posted / matthew
On an autotransformer there is a physical connection
between the primary and secondary and the voltage variation
is not much so the resistence steps are less. The opposite
is true for double wound transformer.
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
33kv Rated output avilable in market (any where in india)
What is voltage divider rule?
what is the difference between megger and earth resister ??
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
what is the criteria for selection of conductor used for ehv ac electrical dischrge
What are the types of transformers according to the arrangement of iron cores?
State the formula for overall efficiency of thermal power station
Load break swicth maintenance procedure.
Explain marx circuit.
what is the function of gss in the dg set.
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
What is line resistance of cable & how it can be measured ?
wat system call?
For a stable system, where should the poles of a system be in a root loci plot?