if we convert ampers into kw,which one formula use by
us,pls tell me?
Answer Posted / pillay
there is no one formula only.
there are some formulas that you must know,,
you must know how to use the correct one when you need it.
for DC power it is always just voltage x current = watts
for AC single phase it is always volt x current x pf = watts
for AC 3 phase it is root 3 x volt x current x pf = watts
the watts than you change to KW or MW if necessary.
this are all for real calculations. when you practice with it often than you will be able to give an estimate bcos the pf varies according to situation.
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
WHAT IS THE PARTIAL DISCHARGE TEST?
What is the meaning of dedicated earthing?
How to know vacuum in vacuum cylinder of breaker in working condition
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
what is the formula to calculate voltage drop/loss on 66KV Transmission Line?
why there using acb enclosure in big buildings
What is the function of attenuator in cro?
what is the Transformer Impedence?How can calculate?
how many types control panel of a 132/33 kv substation
Why negative feedback is preferred in the control system?
1.why should we connect the measuring instruments in l.v side in short circuit test of a transformer? 2.why the power factor is less in open circuit test of a transformer?
Draw the vector diagramme for Asynchronous Induction Generator at noload,half load and fullload.
What is the difference between single point and double point bonding. please kindly detail about bonding of cables.
How may I enrol or get admission to your program?
What happens to a motor if it is connected in Delta connection