can you give main difference between ELCB And RCCB?

Answer Posted / ankur saharia

The term ELCB stands for Earth Leakage Circuit breaker .whenever the leakage current from any live part to ground exceeds a particular value, then the trip coil of ELCB operate for further disconnection of the live part. Generally the trip coil of ELCB is connected in between the non- conducting part of any equipment (Insulation part) and ground. The current setting of a ELCB is in the range of 65mA, 30mSec & must be connected for those loads whose rating exceeds 5KW.
The term RCCB stands for Residual Current Circuit Breaker. The connection of RCCB is always followed by CBCT(Core Balance Current Transformer) .this is because the residual current is sensed by only CBCT.For a 3-phase system, under balanced condition, sum of current at all the phase is zero.i.e. Ia +Ib+Ic =0.but when in any phase comes in contact with earth, then the three phase system is no longer in balance.i.e. Ia+Ib+Ic ≠0(or equal to residual current).this current is sensed by CBCT Secondary & when it exceeds the set value, then is operate & remove that faulty part.

Is This Answer Correct ?    11 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.

1571


You are of electrical field and you are going for software? Why

1856


Define cuttoff frequency?

680


what is charger supervision and control supervision?

1533


EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.

1776






what do you mean by type zero control sytem ?Give an practical example of type zero contol sytem?

1556


it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.

1500


What is a signal flow graph?

647


What is the differentional relay...what is the work of this in power Tx. how it is works..

1453


How to calculate earth fault current for 6.6 KV , 50 HZ , 756 Amps , 3000 RPM , 0.8 PF generator

1620


What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr

653


Either It Possible a dc Motor to Run On Ac Drive [ Ex : ACS 800 , Yaskawa F7 ] If it is Possible How Pls Inform Me dinesh_elect_eng@yahoo.com

1559


hi can any body send me syllabus of rrb electrical section engg... and past pepar also of any board...

2137


what do u understand from filter factor of reactor?

1536


what are types of encoder

1435