The starting current, will be 6-8 times higher than the
motor's rated current because the motor is at rest.
Those starters reduce or diminish this inrush starting
current are called electrical soft starters.
Soft start is one of the facilities available in VVVF
drives. The other facilities are providing higher starting
torque, speed variation, constant torque maintenance soft
stop etc. Simply saying VVVF drive take care of starting
control, speed control, protection control, forwarding,
reversing control and stopping.

Is This Answer Correct ?    16 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.

1406


if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .

1152


how can i get an electrical c-certificate?

1785


what is meant by 3rd hormonics ?

1473


Discuss the effect of sudden loading of an induction motor

1378






Any one can explaination about calibration with rotating sub standards?

1523


how is the incoming cable size calculated for a given current rating of a panel??

1423


Show Details FROM:Muhammed Ikram TO:qa@allinterview.com Message flagged Saturday, June 4, 2011 10:07 PMMessage bodyHello all, i want to ask a question to all of you that what is VMM (voltage monitoring module )? how it work,s? i heard somewhere that it compare 1 phase voltage to other phase voltage. but there is also some setting on it. how to set it,s setting. please tell me briefly. Thank,s and Regard,s. Muhammed Ikram.

1403


i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.

1309


What is the classification of hydro projects based on installed capacity?

675


.php|

1711


How can two 3 phase transformers of same KVA and Voltage be connected in parallel?

1331


What is class ab operation?

623


Form S and "c" license application both are same? @ tneb portal

1252


sir, i am 3 years diploma course pass out candidate.what type of certificate can i got in marine service.

1438