We have isolation transformer 25kvA & ONLINE UPS 15KvA
(3PHASE I/P,3PHASE O/P)where isolation should have
connect,before UPS or after please brief.
Answer Posted / thowsif_emerson
It should be connect before the Input Filter of the UPS..
Pls have a look on this Circuit Diagaram:-
http://www.tpub.com/content/doe2/spec3021/spec30210047.htm
| Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
What are the various types of BUSBAR Schemes? explain each
If we need 4c× 50mm sq cable but it's not available so we can pull 4c×25mm sq two cables?
Starting current of a 10 HP induction Motor is ______ time’s full load current.
For RCD (Residual current device) Icu is defined. How i can find Ics for them?
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
why ten delta testing is carried out on power transformer
AL=0B9H,bl=75H, ADD AL,BL AL=____________? CF________? OF___________?
Why two phase welding machine is used instead of three phase welding machine.
What is the drawback of class b amplifier?
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
3phase cable calculation formula by motor load
how are reversing the direction of rotation of dc motor
Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?
Comment on the working principle of operation of a single-phase transformer.
can anyone explain 11kV 3core cable megger,hi pot test procedure with connection details?