2 hp motar how many amps taken please show me the formula
Answer Posted / gaurang bhavsar- jr. asst. ele
Elect. Power(3-ph)=1.732*V*I*p.f.Now,
2h.p.=2*0.746=1.492=1.5 kw. So, If a voltage system of 3-
ph,415V, 50 Hz is taken, assuming a p.f. of 0.8 then--
1.5=1.732*0.415*I*0.8 which gives I=2.6085 Amp of normal
current. The starting current will be approx. 3 times of
normal current i.e.-7.82 Amp.
Is This Answer Correct ? | 20 Yes | 3 No |
Post New Answer View All Answers
how r charge carriers produced
describe the phenomena of vacuum interruption in C.B
description with working of all parts of a Diesel generator???????
difrent between vcb acb sf6 and mccb breakers
DIFFERENCE BETWEEN NORMAL TRAFO AND THRISTER TRAFO?
what types of cable used in underground coal mining?
what is meant by k-rating in isolation transformer?what is k9, k14 stands for?
what is the formula for calculating the phase clerance between two phases and phase to earth how to calculate the cable for a motor
What is kvar?
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
what do you mean by plant earthing system.
why electron produce magnetic field when it is in motion?
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?
how could we know the size of cable by physical view?