2 hp motar how many amps taken please show me the formula
Answer Posted / gaurang bhavsar- jr. asst. ele
Elect. Power(3-ph)=1.732*V*I*p.f.Now,
2h.p.=2*0.746=1.492=1.5 kw. So, If a voltage system of 3-
ph,415V, 50 Hz is taken, assuming a p.f. of 0.8 then--
1.5=1.732*0.415*I*0.8 which gives I=2.6085 Amp of normal
current. The starting current will be approx. 3 times of
normal current i.e.-7.82 Amp.
| Is This Answer Correct ? | 20 Yes | 3 No |
Post New Answer View All Answers
What is electrical grounding?
what is the use of current transformer in power transformer secondary side.?its connectyed in WTI
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
What is the disadvantage in proportional controller?
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
In CTs tan delta point should be earthed , what is the reason behind it?
How good are you in resolving the commercial issues to Employer's advantage?
working principle of AC Servo Motor with its construction
why u r living from presentaly working.
can we synchronize star system generators with delta system generators?
Explain the working of any one cutting machine
is oil viscosity affect on motor current?
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
what are symmetrical and non symmetrical components in electrical installation.