what is phase to phase voltage? what is line to line voltage
Answer Posted / sankar maiti b.tech ee w.b
Q. what is phase to phase voltage? what is line to line
voltage
Answer:
phase to phaes voltage 440v
line to line voltage is 220v
| Is This Answer Correct ? | 3 Yes | 25 No |
Post New Answer View All Answers
What is the distance between body earthing and neutral earthing.?
Why do we perform an open-circuit test and short-circuit test on the transformer?
What should be current in the Primary and secondary side of 1000KVA (11KV Supply)Transformer.?
Why do we use copper cable for HT Supply and why not Aluminium?
how to check three phase motor torque value?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?