Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

working of bucholz relay of a transformer

Answer Posted / valluru subba rao

Buchholz Relay (found only on transformers with conservators).
The Buchholz relay has two oil-filled chambers with floats
and relays arranged vertically one over the other. If high
eddy currents, local overheating, or partial discharges
occur within the tank, bubbles of resultant gas rise to the
top of the tank. These rise through the pipe between the
tank and the conservator. As gas bubbles migrate along the
pipe, they enter the Buchholz relay and rise into the top
chamber. As gas builds up inside the chamber, it displaces
the oil, decreasing the level. The top float descends with
oil level until it passes a magnetic switch which activates
an alarm. The bottom float and relay cannot be activated by
additional gas buildup. The float is located slightly below
the top of the pipe so that once the top chamber is filled,
additional gas goes into the pipe and on up to the
conservator. Typically, inspection windows are provided so
that the amount of gas and relay operation may be viewed
during testing. If the oil level falls low enough
(conservator empty), switch contacts in the bottom chamber
are activated by the bottom float. These contacts are
typically connected to cause the transformer to trip. This
relay also serves a third function, similar to the sudden
pressure relay. A magnetically held paddle attached to the
bottom float is positioned in the oil-flow stream between
the conservator and transformer tank. Normal flows resulting
from temperature changes are small and bypass below the
paddle. If a fault occurs in the transformer, a pressure
wave (surge) is created in the oil. This surge travels
through the pipe and displaces the paddle. The paddle
activates the same magnetic switch as the bottom float
mentioned above, tripping the transformer. The flow rate at
which the paddle activates the relay is normally adjustable

Is This Answer Correct ?    26 Yes 8 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Can any one know what are the symbols at the down (below) the analog ammeter??? there are 4 symbols which are they ?????

1960


For R-L or R-C ckt,time constant formula is L/R and RC respectively and its unit is in sec.Pls tell me the derivation

3353


Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.

3403


what are the analog quality input for protection function?what are minimum reqiments?

1902


1.what is mean by 8/20 micro sec waveshape

2284


What is a differential amplifier? Also, explain cmrr.

1425


WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM

2055


What is the Basic Difference bitween Long Shunt Connection and Short Shunt Connection in DC Generator?

2393


How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations

2175


How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me

2087


A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.

1119


How do you select the pickup value of the relay?

1377


iam preparing for rrb section engineer post in electrical branch.suggest the right textbook for my reference.fromwhere i will get the previous q.papers?

2337


What is systematic error?

1424


What is the difference between grid and off- grid system??

2000