Answer Posted / shvetang dave
MCB means miniature circuit breaker--It is thermal &
magnetic trip device operating upto 100 A. It's range is
fixed not selectable.
MCCB means Moulded Case Circuit Breaker---It is operated
upto 1000 A and High voltage MCCB also operates on 1200 A
also...And it's range is selectable..
ELCB means Earth Leakage Circuit breaker---It is operated
on leakage current only..It is not operated on short
circuit or overload current.
RCCB means Residual Current Circuti Breaker---it's Working
principle is same as ELCb..It is also operated on Leakage
current..Main differance between it and ELCB is that it is
also operated on Short circuit current
| Is This Answer Correct ? | 50 Yes | 7 No |
Post New Answer View All Answers
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
WHAT IS MEANT BY TV TERMINAL IN 500MVA TRANSFORMER?
DC transmission
3phase cable calculation formula by motor load
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
What is the test block protection relay if any body know plz explained
How RTCC panel is working and give single line diagram for RTCC with transformer?
what topics we have to concentrate for power grid et.written test.and tell what to read for english synonyms and antonyms.
Classify driling machines.
what is spadar bar .why I use in DC generator.
will there be any problem by recovering slip from single phase induction motors?
what & how to check the lightning arrester
diff.between servo motor and ac motor
what is meant by impulse voltage?
The inventer is a battery, but if lost current at home u will turn on the fan but the is AC and inventer battery is dc . Then how the fan was rotating. What device Or machine in fan converst the Dc power to Ac power