Distribution Transformer are connected in configuration?
a. Star/delta b. delta/star
c. star/star d. delta/delta
Answer Posted / dhiraj
delta/star
bcoz from secondary star we can get neutral
Is This Answer Correct ? | 10 Yes | 2 No |
Post New Answer View All Answers
when the time of backcharging the transformer three phases only enough or three phase with neutral is must.from these which one is the best one.
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
Why neutral point is consider as zero potential?
Is there any Electrical supervisor license which gives permit to work whole India rather than individual state??
What type interview questions ask in Electrical technicians
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
Iwould like to know barc interview questions
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
Different types of relay fault which phase sequence??
can u tell me the promotion from oiller to enginer
I have doubt that the supply HZ (very low or high than rated ) may affect the power factor. is it true. ?
what are the principles of a booster converter?
What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance
Define average demand?
What is VSCF windelectrical system?