Answer Posted / chethan
V=415 ,cos=0.8
1HP = 746 Watts
p=1.732*V*cos*I
746=1.732*415*0.8*I
I=746/575.025
Ans.1.297
| Is This Answer Correct ? | 72 Yes | 17 No |
Post New Answer View All Answers
In 11/0.414 KV Parralel supply network with Bus tie closed what will be the fault level is it doubled or halved??
how to calculate cooling requirement of datacentre from electrical load?
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth
Define settling time.
what is PDU in transformer?? which company manufacture??
electrical
In a carnot engine with an efficiency of 40%, the heat rejected to the sink at 27 C is 60 kJ, then the heat supplied in kJ to the engine by the sources is
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
Starting current of a 10 HP induction Motor is ______ time’s full load current.
HOW TO CALCULATE S/C,O/C,E/F OF ACB.
why normally Generator rating are between 11Kv to 22Kv?
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
For group 1 , 2 whather i have to prepare my technical or general studies etc? and im graduate in ee engg. for wht posts im eligible for? please tell me!
i am studying in final year can i allowed for 23rd UES of Indian army