wat is syncronization . wat parameter will take for
syncronization.
Answer Posted / sudheer
when one Generator is running and suppose its rating is
1500 kva/1200 kw,and load increased and we wants to put
more load on GENERATOR . So then we have to run second
generator and to be shift some load on second generator,
otherwise the generator will be over loaded and tripped on
over-load fault. when we connect two generators parrallel,
this arrangement is called synchronisation.we connect the
out-put supply of both generators parallel by
synchronisation.In synchronisation we have to match these
parameters--phase sequence, frequency and voltage.when all
three parameters match we ON the breaker and
synchronisation complete and now we can put more load
(about 2000 kw) on generator.
| Is This Answer Correct ? | 17 Yes | 1 No |
Post New Answer View All Answers
explain types of electric welding and its applications
and gate circuit diagram,amplifier circuit diagram
What does ampere turns shows?
how can tell us the AC indoor or outdoor which Tr and formulls
How does "OUT OF STEP" relay ,for Synchronous motor protection, work?
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
why the check zone and main zone are used for Busbar Protn. scheem?
how to CHECK CT AND PT AT THE FAULT OCCUR IN GENERATOR RELAY PANEL .
What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker
what is the condition for YnD11
What is Negative Potential Bias
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5
how can we change the phase angle b/w two phase?
WHAT IS VCB SAFETY