what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?
Answer Posted / duraivelu j
there are two type of ct. one is metering ( class 0.1,class
0.5,1,&5)another one is Protection (PS, 5P10,5P20)the
metering ct has very less error, so we can measure actual
power by accuratly,the protecton ct has more error but that
has more saturaion level, so during fault condition this ct
will not saturate. bur Metering ct will saturate when fault
condition and that time we can't measure the current vale.
| Is This Answer Correct ? | 183 Yes | 17 No |
Post New Answer View All Answers
BRIEFLY EXPLAIN THE STORAGE CLASSES AND THEIR TYPES IN C
What do you mean by the zone of protection?
Determine a suitable number of slors and conductors per slot for the starter 1 winding of a 3 phase, 3300 V. SO Hz 300 rpm alternator. The diameter is 2.3 m
what is the difference between droop mode and ischnorous mode in thermal powerplant?
witch pump used in wtp
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB Machines of higher rating?
How to select transmission line type (i.e. 11kv or 33kv) for new established industries
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
What do you mean by screen of power cables?
how to calculate compresor capacity?
I am completed DEEE in tamilnadu, now i am working in andhrapradesh with 2.5 year experience in relavent field. capacity of the tranformer is 11KV, 1MVA Transformer, i am eligible for getting c licence in andhrapradesh pl help me.
What are the components of feedback control system?
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?
What are the applications of the electric motors?