How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation

Answer Posted / govind bisht

Assume PF of transformer is .8.
rating of transformer=1500kVA=1500X.8=1200kW
V=433(3phase)
So that maximum current-
I= P/V*PF
=1200*1000/1.732*433*.=1600A
So cable size required if copper cable
1mm=4amp= 400sqmm(by consedering all factors)
For aluminium cable
1mm=2.5A=640sqmm

Is This Answer Correct ?    61 Yes 109 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How many types of instrument cables are there?

642


what is tri state logic gate

1632


How many types of interlocking use in screw type air compressor,make-Kaser(BSD MODEL)?

1619


What are the protection required for Transformer, motor, Line, Generator, capacitor, that all i have to refer which standard?(Like Transformer detail IS 2026)

1496


why i can not use thimble on capacitor duty contactor

898






what is the effect of un-synchronized power.

1560


why Induction Generators are not "Black start" ? and apart from WTGs where this types of generator are generally used?

2235


how to discharge 3 phase power factor correction capacitors

1980


what may the reason for vector shift in a generator?

1419


If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.

1728


What is Instantaneous Earth fault relay,how will work

1702


What are the different types of transformers?

672


what is high and low cut off voltage of BB and DG at SPS????????

1018


how can found motors folt current ? how can disided circuit breakers caoicity and breaking capicity ?

1634


Why two phase welding machine is used instead of three phase welding machine.

1401