Answer Posted / manish meena
bucholz relay is oil and gas operated protective relay
which is mounted on the pipe between transformer tank and
conservator
so when during any fault result in gas formation this will
cause the oil level in relay to drop and makes the alarm
contact to operates if the fault is very severe then the
gas formation will be very large due to this there is
further decrease in level of oil in relay..due to this trip
contacts are operated and finally the transformer is
disconnected from the supply....
| Is This Answer Correct ? | 41 Yes | 6 No |
Post New Answer View All Answers
Define de-sensitivity?
Explain the operation of grid connected central solar inverter ?
what is the effect of change in supply frequency on load angle of synchronous motor,all other parameters remaining same?
Meaning of ingrace protection for motor.for ex IPXY
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr
What is the end effect of linear induction motor ??
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
Difference between rating factor of cable and derating factor of cable?
WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ
What is the difference between diode and a transistor in terms of the direction of current flow?
What are motor generator sets and explain the different ways the motor generator set can be used ?
What is ramp signal?
LET ME NOW MORE ABOUT icu and ics for circuit breaker. how we calculate the rating of circuit breaker and i c u and ics values
What will happened if the neutral of the (star connected secondry) Xformer disconnected? (if its Above KVA rated one)
HOW TO REDUCE POWER PLANT AUXILIARY POWER CONSUMPTION?