What is the differance between negative dc voltage and
positive dc voltage because some circuit uses -24,-5,-12,-
15,volt dc supply
Answer Posted / alok gangwar
A negative line voltage helps to reduce the corrosion from
electrochemical reactions occurring on a wet telephone
line. Also -48v DC is more stable than +48 volit, so -48 V
is preferred.
| Is This Answer Correct ? | 32 Yes | 7 No |
Post New Answer View All Answers
should %impedance be high or low in a power transformer? if so why?
draw the restricted earth fault protection circuit install on power transformer and identify its parameters and draw C/C curve of it
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
how to calculate magnetic force genrated by a coil ?
what is the relation between knowing of the distance between power transformer and the capacitor feeder in case of parallel operation
What is the resonant peak?
Why it is possible to use PWM with a STATCOM and not with a conventional TCR based SVC
What is the emf equation of a transformer?
we specify current in case of feeder but in case of distributor voltage, why?
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?
why we use circuit breakers for switching instead of normal switching device?
What is slip in an induction motor?
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.