how we are measuring the winding temperature of the
transformer?
Answer Posted / sunil
winding temp means temp. of oil plus additional temp
measure due to load
| Is This Answer Correct ? | 8 Yes | 4 No |
Post New Answer View All Answers
can we conduct the swineburne's test on a dc series motor? why?
If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.
what is the function of capacitor duty contactor in an capacitor panel???
Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?
What safety precaution are to be taken for avoiding electric hazards ?
What is the difference between isolators and electrical circuit breakers? What is bus-bar?
what is destructive and non-destructive testing of welding
Explain using drawings what is reverse PID action w.r.t PID controllers.
Why collecting electrode of ESP to be earthed
1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai
Can you explain about pole discrepancy scheme
What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?
Difference between Lugs and Thimbles
can u describe the method used for protection of transmission line.
What is the phase relationship between the primary and secondary voltages of a transformer?